Re: [EnergyPlus_Support] setpoint



It is certain that the HVAC system is limited in capacity.  This could be due 
to many different reasons:  airflow rate too small, cooling coil size too 
small, chiller capacity too small, supply air setpoint too warm, chilled water 
setpoint too warm, component or system scheduled off, etc.  If you are not 
certain what the component sizes should be, I would suggest using autosizing.  
See the 5ZoneAuto example.

Mike


On 8 Jun 2004, at 5:15, pizzaalan wrote:

> Hi, dear all
> 
> I simulated a building and used single duct VAV with reheat. I 
> specified the zone thermostats to control the zone temperatures. 
> However, the mean air temperatures are not even close to the 
> setpoints (in summer condition, it is 50C while setpoint is 30C). 
> Also I change the setpoints, but the mean air temperatures won't 
> change at all. 
> 
> I just create my file by looking at the example 
> file "SingleDuctVAVReheat". What mistakes do I probably make?
> Is the norminal capacity of purchased chilled water too small?
> 
> 
> Thanks in advance.
> 
> Sincerely,
> Alan
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/