Re: [EnergyPlus_Support] Load
EnergyPlus's talking about sensible load all the time,
for example autosizing has no latent load included.
But in coil setup, there is a outlet air humidity,
which to me that latent load is also calculated. Does
this mean that the sizing will be smaller than
actually needed (total load) in summer design day, and
therefore a larger sizing factor has to be assigned in
Miami than in Phoenix?
If I want E+ to calculate latent load energy, is it
must to have humidity setpoint in the space?
Hannah
--- "Richard J. Liesen" <rliesen@xxxxxxxx> wrote:
> At 01:52 PM 6/17/2004, Hannah Yan wrote:
> >What is the difference between Zone/Sys Sensible
> Load
> >Predicted and Zone/Sys Sensible Cooling Rate ( or
> >heating rate)?
>
> The predicted Load is the load that would be
> necessary to bring the current
> zone conditions to the setpoint.
>
> The Zone/Sys Sensible Cooling Rate is the actual
> amount of heating or
> cooling the system could provide with its given
> capacities in that time step.
>
> If the predicted is not equal to the corrected than
> most likely the system
> was not large enough, but there are times when due
> to things like outside
> air that it can be larger than predicted. Whatever
> is not handled in the
> given time step will be addressed in the next time
> step. If the system is
> not large enough this would show up as a higher
> temperature in the zone
> than the setpoint.
>
> >Why is ZONE1:Zone/Sys Moisture Load Rate
> >Predicted[kgWater/sec] zero?
>
> This means that there is NO Humidistat assigned for
> that zone. Without a
> Humidistat there is no setpoint and thus no
> predicted moisture load.
>
>
> Thanks
> Dr. Richard Liesen
> Associate Director, Building Systems Laboratory
> Department of Mechanical and Industrial Engineering
> University of Illinois at Urbana-Champaign
>
>
>
__________________________________
Do you Yahoo!?
New and Improved Yahoo! Mail - 100MB free storage!
http://promotions.yahoo.com/new_mail
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/