At 01:52 PM 6/17/2004, Hannah Yan wrote:
>What is the difference between Zone/Sys Sensible Load
>Predicted and Zone/Sys Sensible Cooling Rate ( or
>heating rate)?
The predicted Load is the load that would be necessary to bring the current
zone conditions to the setpoint.
The Zone/Sys Sensible Cooling Rate is the actual amount of heating or
cooling the system could provide with its given capacities in that time step.
If the predicted is not equal to the corrected than most likely the system
was not large enough, but there are times when due to things like outside
air that it can be larger than predicted. Whatever is not handled in the
given time step will be addressed in the next time step. If the system is
not large enough this would show up as a higher temperature in the zone
than the setpoint.
>Why is ZONE1:Zone/Sys Moisture Load Rate
>Predicted[kgWater/sec] zero?
This means that there is NO Humidistat assigned for that zone. Without a
Humidistat there is no setpoint and thus no predicted moisture load.
Thanks
Dr. Richard Liesen
Associate Director, Building Systems Laboratory
Department of Mechanical and Industrial Engineering
University of Illinois at Urbana-Champaign
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/