Re: [EnergyPlus_Support] Question about Cooling Tower



The autosizing usually works best when you autosize everything.  Go back to 
that run and look at the sizing reports in the eio output file.  Did the zones 
show a cooling load?  Did the chilled water coils size to a nonzero water flow 
rate?  Did the chiller condenser water flow rate size to a nonzero value?  Did 
the condenser loop flow rates size to a nonzero value?  If you find a zero size 
at some point along the way, then you need to check the inputs related to that 
part of the system.

Mike


On 17 Jun 2004, at 10:14, carmen herrero prada wrote:

> Mike and Edward,
> 
> thanks a lot for your comments but, unfortunately I
> cannot find out what is going on. Mike, you are right,
> there was some problem with the sizing. I was trying
> to autosize everything (zones, system and plants) at
> the same time, and i should maybe try to autosize
> first the zone, then system and then plant (am I
> correct?). So for that, I set some values of the
> system and the plant in order to autosize the zones,
> but then I keep getting this fatal error message:
> 
> **  Fatal  ** Node MassFlowRateSetPoint = 0.0,
> Node=ESTE OUTLET NODE
> 
> ESTE OUTLET NODE is an air node just at the outlet of
> the air primary loop (just after the heating
> coil)which consist of an outside air mixer, fan,
> cooling coil and single zone reheat coil.
> 
> I have even tried to set the maximum branch flow rate
> to 1.3 m3/s in the air primary loop branch object
> instead of autosizing it, but it keeps giving me the
> same error message.
> 
> Any suggestions?
> 
> Thank you very much.
> 
> Carmen.
> 
> 
> 
> 
> --- "Michael J. Witte" <mjwitte@xxxxxxxx> escribió: 
> ---------------------------------
> There is something wrong with the sizing inputs,
> because the condenser water 
> pump flow rate is being sized to zero.  You should be
> able to autosize the 
> entire condenser loop and all of its components and it
> will automatically match 
> the chiller's condenser water flow rate.  See p. 317
> (pdf p. 345) of the Input 
> Output reference, Item 4. 
> 
> Mike
> 
> 
> On 15 Jun 2004, at 18:20, carmen herrero prada wrote:
> 
> > Hello all,
> > 
> > I am having some problems while simulating condenser
> > loop water cooled with a cooling tower. I am
> > autosizing everything (plant sizing), except the
> > Design Water Flow rate (m3/s) which has to be the
> same
> > that appears in the chiller object, in the field:
> > Design Condenser Volumetric Flow rate (m3/s)
> > 
> > But, althouth I have tried with different options
> (as
> > creating a schedule for a Condenser Temperature
> > Setpoint node in the Condenser Loop object or just
> > typing AIR to use the outdoor air wet-bulb as the
> > setpoint, as i have seen in the example files) I
> keep
> > getting the same errors:
> > 
> > ** Warning ** Check input. Pump nominal power or
> motor
> > efficiency is set to 0, for pump=CONDPUMP
> >    ** Warning ** Check input. Pump nominal
> volumetric
> > flow rate is set or calculated = 0, for
> pump=CONDPUMP
> >    ** Severe  ** COOLING TOWER:SINGLE SPEED "TOWER".
> > Free convection air flow rate must be less than the
> > design air flow rate.
> >    ** Severe  ** COOLING TOWER:SINGLE SPEED "TOWER".
> > Free convection UA must be less than the design
> tower
> > UA.
> >    **  Fatal  ** Errors found in Cooling Tower input
> > 
> > 
> > I do not understand what is going on. I have also
> > autosized the condenser pump and I have tried by
> > changing the exit temperature and the delta
> > temperature in the plant sizing object for the
> > condenser plant.
> > 
> > I am sure i am missing something. Could anybody tell
> > me what it is?
> > 
> > Thanks a lot,
> > 
> > Carmen.
> > 
> > 
> > 
> >
> ______________________________________________________________________
> > Yahoo! lanza su nueva tecnología de búsquedas
> > ¿te atreves a comparar?
> > http://busquedas.yahoo.es
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files
> to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups..yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files
> to the appropriate folder in the Files area of the
> Support Web Site.
> 
> 
> 
> Yahoo! Groups Sponsor  ADVERTISEMENT
> 
> 
> ---------------------------------
> Yahoo! Groups Links
> 
>    To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>    To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>    Your use of Yahoo! Groups is subject to the Yahoo!
> Terms of Service.
> 
> 
> 
> 
> ______________________________________________________________________
> Yahoo! lanza su nueva tecnología de búsquedas
> ¿te atreves a comparar?
> http://busquedas.yahoo.es
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 





------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/