The HVAC equipment availability uses zSCHEDULE-12.  This schedule is always 
negative, so the equipment is always off.

Some other issues I noticed:

1.  The heating and cooling setpoint temperature schedules are still in deg. F. 
 You must convert these by hand to deg. C.  

2.  The furnace system is serving the attic with supply air.  My guess is that 
is should not be.

3.  Surfaces CEILIN-1-ADJACENT and CEILIN-2-ADJACENT are set to surface type 
FLOOR.  They should be CEILING.

Mike


On 30 Jun 2004, at 12:46, Zhang, Weihua wrote:

> Hi,
> 
> I send an email about using the translation program to convert DOE-2 residential
> building input to E+ input. Since no system input from DOE-2 input was
> translated to E+, I added a system input from "FurnaceWithDXSystem-TE" file from
> the template folder. I also patched a lot of missing information in order to
> complete a simulation run. I was able to able to go ahead with the simulation.
> However, when I looked at my Annual Building Utility Performance Summary in the
> form of HTML, everything is blank. I don't think the warnings could have caused
> this. 
> 
> I posted the DOE-2 input as well as the Energy Plus input file in a zip file
> called case0m-4.
> 
> wei   
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
     http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
     EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
     http://docs.yahoo.com/info/terms/