Re: [EnergyPlus_Support] Glare index



My guess is that the coordinates or facing angle of the daylighting reference 
point in these zones is incorrect.  Remember that daylighting reference points 
are always relative to the zone origin, even when World Coordinates have been 
specified.  In the dxf drawing file, the daylighting reference points are drawn 
as a small red circle to help you verify the location.  You may need to comment 
out all of the daylighting objects and then add them back one by one to make 
sure each reference point is within the appropriate zone.  If you are unable to 
resolve this, please submit your input file.

Mike




On 8 Jul 2004, at 4:26, leeslwong wrote:

> Hi,
> 
> I've simulated the daylight performance of a residential block which 
> includes a kitchen, a living room, 2 bedrooms and a master bedroom. I 
> called out the annual glare index with hourly basis of each rooms. 
> The results show that there is no glare (means '0') in the kitchen, a 
> bedroom and a living room. What situations would have these results? 
> But there are glare index in other two rooms. Those five room have a 
> window facing with the same direction (east). As I know glare index 
> never reaches '0'. Anybody can tell me what's happening and how to 
> solve it?
> 
> Thanks
> 
> lee
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/