Re: [EnergyPlus_Support] dalighting fields



I am not sure that I understand your question.  The required illuminance level 
for the occupants would be determined from a lighting handbook depending on the 
type of activity.  The illuminance produced by a given wattage of artificial 
lighting is dependent on the fixture type and placement.  EnergyPlus does not 
simulate the illuminance level produced by the LIGHTS object.  If you are using 
the DAYLIGHTING controls, EnergyPlus assumes that the LIGHTS objects in the 
zone are capable of meeting the illuminance setopint at full output.  It is up 
to the user to ensure the power level is adequate.

Mike


On 19 Jul 2004, at 2:01, iris_lilin wrote:

> hi, can i check with you how to obtain the artificial lighting 
> illuminance value??
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/