Re: [EnergyPlus_Support] Simple mechanical ventilation



May I ask why you do not want to use the VENTILATION object?

There is no simple HVAC component to do what you want.  The two easiest would 
be a ENERGY RECOVERY VENTILATOR:STAND ALONE with the heat recovery 
effectiveness set to zero, or a AIR CONDITIONER:WINDOW:CYCLING with a dx 
cooling coil that is always scheduled off.

Mike


On 19 Jul 2004, at 13:03, Andy Tindale wrote:

> Can anyone advise me on the simplest way to specify mechanical (forced)
> ventilation, without using the VENTILATION object?
> 
> I have looked at the 'unitary ventilator' and the 'window ac' objects and
> wondered which of these is easier bearing in mind I don't want to specify any
> plant, branches, heating and cooling coils etc.  I couldn't find any example
> files which used these objects without heating and cooling.
> 
> Thanks in advance
> Andy Tindale
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/