Re: [EnergyPlus_Support] about "Purchased air" RH setpoint
My apologies for the late addition here.
PURCHASED AIR is a very simple system. Two issues that may present a problem
for you here:
1. When using the outside air ventilation rate with PURCHASED AIR, if the zone
load is small and requires a supply air flow less than the specified outside
air flow rate, then the OA will be reduced.
2. PURCHASED AIR supplies air to the zone at a specified humidity ratio. The
latent load to provide this is reported as part of Purchased Air Total Cooling
Energy (or Rate). Because PURCHASED AIR does not maintain the zone at a
specified RH setpoint, I believe that summing the "Zone/Sys Moisture Load Rate
Predicted" will be incorrect. Whatever latent load is not met in the current
timestep will appear again as part of the moisture load predicted in the next
timestep.
Mike
On 28 Jul 2004, at 7:23, Richard Raustad wrote:
> See object ZONE CONTROL:HUMIDISTAT for calculating latent cooling load
> and use the predicted moisture load to view the result:
>
> Report Variable,
> *, !- Key_Value
> Zone/Sys Moisture Load Rate Predicted, !- Variable_Name
> timestep; !- Reporting_Frequency
>
>
>
>
> Zheng Li wrote:
>
> > Dear all:
> >
> > I am using the "Purchased air" to calculate a living/dining room
> > cooling load in summer design day with and without the outside air
> > ventilation rate, i.e., 7.5liter/per person. I want to compare the
> > difference of the sensible and latent cooling load under these two
> > conditions. I have put the indoor temperature setpoint 24C as a
> > "SCHEDULE" and the "ZONE CONTROL: THERMOSTATIC"into the IDF editor,
> > but how can I make a setpoint for indoor RH, i.e., 50% at the same
> > time? Without the RH setpoint, EP also can calculate the cooling load,
> > is there a default RH setpoint in EP? If yes, where and how can I
> > change it value?
> >
> > I am waitting for the answer.
> >
> > Thanks a lot!
> >
> > LI
> >
> >
> > ---------------------------------
> > ¥þ·s Yahoo! Mail - 100 MB §K¶O¹q¶lÀx¦s¶q
> > mail.yahoo.com.hk
> >
> > [Non-text portions of this message have been removed]
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the
> > appropriate folder in the Files area of the Support Web Site.
> >
> >
> >
> > Yahoo! Groups Sponsor
> > ADVERTISEMENT
> > <http://us.ard.yahoo.com/SIG=129iga6vr/M=295196.4901138.6071305.3001176/D=grou
> > ps/S=1705007389:HM/EXP=1091095998/A=2128215/R=0/SIG=10se96mf6/*http://companio
> > n.yahoo.com>
> >
> >
> >
> > ------------------------------------------------------------------------
> > Yahoo! Groups Links
> >
> > * To visit your group on the web, go to:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > * To unsubscribe from this group, send an email to:
> > EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
> > be>
> > * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > Service <http://docs.yahoo.com/info/terms/>.
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Yahoo! Domains - Claim yours for only $14.70
http://us.click.yahoo.com/Z1wmxD/DREIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/