Re: [EnergyPlus_Support] about the nodes, again!
Thank you for sending the input file. The problem is in the VAV unit outlet
node name:
> SINGLE DUCT:VAV:REHEAT,
> RF-INT1 VAV system, !- Name of System
> AirSysAvailSched, !- System Availability schedule
> Zone 13 Reheat Air Inlet Node, !- DAMPER Air Outlet Node
> Zone 13 Damper Inlet Node, !- UNIT Air Inlet Node
<snip>
> RF-INT2 Inlet Node, !- UNIT Air Outlet Node
> 0.00025, !- Convergence Tolerance
> NORMAL; !- Damper Heating Action
It should be "RF-INT1 Inlet Node". I will submit a suggestion to attempt to
make the error message more meaningful in this case.
However, with this fixed, the simulation runs but produces many max iteration
errors. I do not know why yet.
Mike
On 11 Aug 2004, at 3:49, beyangj wrote:
> Dear Mike,
>
> Thank you very much about your help. Now I still don't know how to
> deal with the problem. I have defined as follow, and the 'Zone 13
> Damper Inlet Node' appear two time, as follow:
>
> AIR PRIMARY LOOP,
> VAV Sys 1,
> VAV Sys 1 Controllers,
> VAV Sys 1 Avail List,
> autosize,
> VAV Sys 1 Branches,
> ,
> Air Loop Inlet Node 1,
> Return Air Mixer Outlet 1,
> Zone Equipment Inlet Node 1,
> Air Loop Outlet Node 1;
>
> ZONE SUPPLY AIR PATH,
> Zone Supply Air Path 1, !- Supply Air Path Name
> Zone Equipment Inlet Node 1, !- Supply Air Path Inlet Node
> Zone Splitter, !- KEY--System Component Type 1
> Splitter 1; !- Component Name 1
>
>
> ZONE SPLITTER,
> Splitter 1, !- Splitter Name
> Zone Equipment Inlet Node 1, !- Inlet_Node
> Zone 1 Damper Inlet Node,!- Outlet_Node_1
> Zone 2 Damper Inlet Node,!- Outlet_Node_2
> Zone 3 Damper Inlet Node,!- Outlet_Node_3
> Zone 4 Damper Inlet Node,!- Outlet_Node_4
> Zone 5 Damper Inlet Node,!- Outlet_Node_5
> Zone 6 Damper Inlet Node,!- Outlet_Node_6
> Zone 7 Damper Inlet Node,!- Outlet_Node_7
> Zone 8 Damper Inlet Node,!- Outlet_Node_8
> Zone 9 Damper Inlet Node,!- Outlet_Node_9
> Zone 10 Damper Inlet Node, !- Outlet_Node_10
> Zone 11 Damper Inlet Node, !- Outlet_Node_11
> Zone 12 Damper Inlet Node, !- Outlet_Node_12
> Zone 13 Damper Inlet Node, !- Outlet_Node_13
> Zone 14 Damper Inlet Node, !- Outlet_Node_14
> Zone 15 Damper Inlet Node, !- Outlet_Node_15
> Zone 16 Damper Inlet Node; !- Outlet_Node_16
>
> SINGLE DUCT:VAV:REHEAT,
> RF-INT1 VAV system, !- Name of System
> AirSysAvailSched, !- System Availability schedule
> Zone 13 Reheat Air Inlet Node, !- DAMPER Air Outlet Node
> Zone 13 Damper Inlet Node, !- UNIT Air Inlet Node
> autosize, !- Maximum air flow rate {m3/s}
> 0.3, !- Zone Minimum Air Flow Fraction
> Zone 13 Reheat Water Inlet Node, !- Control node
> COIL:Water:SimpleHeating,!- Reheat Component Object
> Reheat Coil Zone 13, !- Name of Reheat Component
> autosize, !- Max Reheat Water Flow {m3/s}
> 0.0000000E+00, !- Min Reheat Water Flow {m3/s}
> RF-INT2 Inlet Node, !- UNIT Air Outlet Node
> 0.00025, !- Convergence Tolerance
> NORMAL; !- Damper Heating Action
>
> All the zone Damper Inlet Nodes(From Zone 1 Damper Inlet Node to
> Zone 16 Damper Inlet Node ) are defined at the same way, but the
> complier only gave the Severe message for Zone 13 Damper Inlet Node,
> as follow:
> ** Severe ** Node ZONE 13 DAMPER INLET NODE connects to no component
> ** ~~~ ** Occurs in Supply Air Path=ZONE SUPPLY AIR PATH 1
> ** Fatal ** Preceding errors cause termination
>
> I have checked many times, and I still can't deal with the problem.
> Could you help me?
>
> Thanks a lot!
>
> Stewart
>
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/