Re: [EnergyPlus_Support] Radiant Slab Outside Environment



1.  Yes.  

2. You can ignore the error message.  

3.  If you have both and air system and a radiant system, then the air system 
will control to MAT if it is able.

Mike

On 23 Aug 2004, at 12:37, zhen tian wrote:

> Hi, Mike
> 
> Thanks for your reply.
> 
> I still have some question for this problem.
> 
> First, from your method, the zone with radiant slab on the ceiling and floor is
> treated as a "middle zone", as discribed in the "InputOutput Reference", is it
> right?
> 
> Second, according to your method, I got a severe error from the  error report
> but I can got the simulation result. The error report is:
> 
> "Severe  ** CAUTION -- Interzone surfaces are usually in different zones
>    **   ~~~   ** Surface=OBJ:0147, Zone=3_P_W
>    **   ~~~   ** Surface=OBJ:0150, Zone=3_P_W"
> Object 147 is the zone floor and Object 150 is the zone ceiling. I set the
> outside environment of Object 147 as Object 150 using the "Other Zone Surface"
> option. And the outside environment of Object 150 as Object 147.
> 
> So what is wrong for this setting? Or can I omit this error?
> 
> The third quesiton is more complex.  The zone imulated is a internal zone (no
> surface contacts outside environment) and thermostat setpoint is 22 degree C. 
> But no matter I use MRT, MAT or Operative.  The zone air temperature is around
> 22 degree C, while the MRT varies.  From my field measurement data, the indoor
> air temperature changes too.  Sounds like Energyplus still take Air Temperature
> as the setpoint.  Otherwise the air temperature will vary if I use MRT or
> Operative as the temperature control type. If my guess is right?  The zone is
> controlled by air system too (with very low air flow rate to let the radiant
> system run).
> 
> Thank you very much for your help.
> 
> Best regards,
> 
> Zhen
> 
> 
> 
> 
> 
> 
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> When the outside environment is set to OtherZoneSurface, EnergyPlus forces the
> outside surface temperature to equal the inside surface temperature of the
> specified OtherZoneSurface.  Making the surface containing the cooling system
> adiabatic will only be valid if the construction of that surface is symmetrical
> and the cooling source is in the center of the construction.  
> 
> Is there a radiant cooling slab in between all of the floors?  If so, you can
> set the exterior environment of the 2nd level floor to be the 2nd level ceiling,
> and set the exterior enviorment of the 2nd level ceiling to be the 2nd level
> floor.  This creates a situation where two surfaces in the same zone are
> connected as interzone surfaces.  If the situation truly repeats itself, this
> can be a valid approach.
> 
> Mike
> 
> 
> On 19 Aug 2004, at 12:15, zhen tian wrote:
> 
> > Hi:
> > 
> > I am simulating a multi-floor building with radiant slab cooling system.  The
> > radiant floor is between two floors.  But I only want to simulate one floor.
> > For example, the radiant slab is between 2 and 3 floor.  I only want to
> > simlate the 2th floor.  So how can simulate the 2th floor without simulating
> > the 3rd floor?  Since the radiant floor will have effect on the 3rd floor and
> > the 3rd fllor is conditioned too. Can I define the foor as adiabatic surface? 
> > Or how can I define the outside environment for the slab surface?
> > 
> > Thanks a lot.
> > 
> > Regards,
> > 
> > Zhen
> > 
> > 
> > ---------------------------------
> > Do you Yahoo!?
> > New and Improved Yahoo! Mail - Send 10MB messages!
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> 
> 
> Yahoo! Groups SponsorADVERTISEMENT
> 
> 
> ---------------------------------
> Yahoo! Groups Links
> 
>    To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>    To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> 
> 
> 
> ---------------------------------
> Do you Yahoo!?
> Win 1 of 4,000 free domain names from Yahoo! Enter now.
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 






------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/