Do you have equipment serving the zone other than the radiant system? The
MRT/MAT/OT choice only applies to the radiant system. If there is other
equipment in the zone, then it will always control to MAT. If this does not
clear things up, please send your input file (zipped) to energyplus-
support@xxxxxxxx or upload it to the yahoo group files area.
Mike
On 24 Aug 2004, at 14:05, zhen tian wrote:
> Sorry, Mike:
>
> I think I don't wholy catch what you mean.
>
> In my field measurement. The room thermostat is set to 22 degree. The measured
> air temperature is 21.8, the Operative is 21.5, so the MRT is 21.2. But in the
> simulation, the air temperature stays at 22, with zone therostat set at 22, no
> matter I set as MRT, MAT or Operative as temperature control type. Can I
> control the air temperature to under 22 with same thermostat setting?
>
> Thanks.
>
> Regards,
>
> Zhen
>
>
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
>
> 3. If you have both and air system and a radiant system, then the air system
> will control to MAT if it is able.
>
> Mike
>
> On 23 Aug 2004, at 12:37, zhen tian wrote:
>
> > The third quesiton is more complex. The zone imulated is a internal zone (no
> > surface contacts outside environment) and thermostat setpoint is 22 degree C.
> > But no matter I use MRT, MAT or Operative. The zone air temperature is around
> > 22 degree C, while the MRT varies. From my field measurement data, the indoor
> > air temperature changes too. Sounds like Energyplus still take Air
> > Temperature as the setpoint. Otherwise the air temperature will vary if I use
> > MRT or Operative as the temperature control type. If my guess is right? The
> > zone is controlled by air system too (with very low air flow rate to let the
> > radiant system run).
>
>
>
> ---------------------------------
> Do you Yahoo!?
> Yahoo! Mail - 50x more storage than other providers!
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/