Re: [EnergyPlus_Support] Re: EnergyPlus validation
Thanks for the update!
Mike
On 25 Aug 2004, at 1:15, johnrham39042 wrote:
> I have have done some benchmarks of EnergyPlus against some of the
> OSU data. I found it to be time well spent as I learned a lot about
> EnergyPlus and the sensitivity to the various input parameters.
>
> The results are similar to those reported in the 2003 ASHRAE paper
> by Chantrasrisalia, Lu, Fisher and Eldridge. The OSU test building
> has a lot of window area and relatively high air flow rates. The
> results are sensitive to the radiative heat transfer properties and
> also to the inside convection cooeficient. The the CeilingDiffuser
> model for inside surface heat transfer seems to work well. Both the
> cooling load and the floor surface temperatures matched the
> experimental data very well.
>
> John Hamilton
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Earl Eiland" <eee@n...>
> wrote:
> > I'm enbarking on a research project where knowing how EnergyPlus
> > predictions relate to actual measured performance will be helpful.
> > some work on that topic has been done at OSU. Does anyone know of
> > other relevant work?
> >
> > Earl Eiland
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/