Re: [EnergyPlus_Support] COMIS venting modulation



This is a bug in version 1.2.0.029.  There are three COMIS report variables 
that are incorrectly summing instead of averaging.  In the rdd file, these are 
listed as:  

Zone,Sum,Opening Factor Multiplier for COMIS Venting Modulation[]
Zone,Sum,Inside Temp Setpoint for COMIS Venting[C]
Zone,Sum,Venting Availability[]

To see the expected values for these variables, you must report them at the 
"timestep" reporting frequency.  

This has been fixed for the next release (CR#6362).

Mike


On 30 Aug 2004, at 14:42, Fernando Simon Westphal wrote:

> Hello,
> 
> We are doing a single zone exercise with the COMIS module in the EnergyPlus. Our
> model has 10x10x3.0 meters and 2 windows in opposite walls. Each window has16 m²
> of area.
> 
> Analysing the outputs, we got values 6 and -6 for the "Opening Factor
> Multiplier for COMIS Venting Modulation". But the Input Output Reference
> (pag. 311, pdf 339, table 14) lists values -2, -1 and 0.0 to 1.0 for this
> variable.
> 
> Could anyone explain about the meaning of 6 and -6 values for this variable?
> 
> Thanks,
> Fernando S. Westphal
> Federal University of Santa Catarina, Brazil
> 
> 
> 
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 






------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/