A major problem with this run is that all of the non-window surfaces are made
up of MATERIAL:REGULAR-R, so there is no thermal mass in this building. This
can cause an unstable solution resulting in a temperature out of bounds error.
Use MATERIAL:REGULAR for all material types except very light insulation
layers. This should solve the problem.
Mike
On 2 Sep 2004, at 14:05, Linda Lawrie wrote:
> You could send your weather file to me directly -- I don't think there is
> enough space to upload it to the files area.
>
> In this case, it appears that your weather environment is causing a problem.
>
> I also note that your floor (at least one) is upside down. This can cause
> significant problems as well.
>
> I will also try a run in a significantly warmer climate that may be closer to
> Lisbon.
>
> At 01:25 PM 9/2/2004, Leila Henriques wrote:
>
> >My fatal error is
> >
> > ** Warning ** Inside surface heat balance did not converge with Max Temp
> > Difference [C] =0.474 vs Max Allowed Temp Diff [C] =2.000E-003
> > ** ~~~ ** occuring in simulation=ACR LISBOA WMO#= at 01/22 16:10
> > ** Severe ** Temperature out of bounds (260.98) for surface=PISO
> > 04:ZN001 TECTO
> > ** ~~~ ** occuring in simulation=ACR LISBOA WMO#= at 01/22 16:20
> > ** ~~~ ** A temperature out of bounds problem can be caused by
> > several things. The user
> > ** ~~~ ** should check the weather environment, the level of
> > internal gains with respect
> > ** ~~~ ** to the zone, and the thermal properties of their
> > materials among other things.
> > ** Fatal ** EnergyPlus has exited due to the reason stated above
> >
>
> Linda
>
> EnergyPlus WebSite: http://www.energyplus.gov
> Owner: EnergyPlus_Support list
> Member: EnergyPlus Development Team
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/