Re: [EnergyPlus_Support] temperature
It is difficult to say for sure, but my guess is that there is some internal
gain (PEOPLE, LIGHTS, ELECTRIC EQUIPMENT, etc.) that has a schedule error. To
help narrow down the cause, the following REPORT VARIABLES may be helpful,
reported hourly: People-Total Heat Gain, Lights-Total Heat Gain, Electric Eq-
Total Heat Gain, Gas Eq-Total Heat Gain.
Mike
On 13 Sep 2004, at 14:19, beyangj wrote:
> Dear,
>
> In a simulation for the whole year, the temperature in the
> controlled zones in summer is the value as I wish, but the
> temperature in the same controlled zones is not reasonable. I set
> the temperature in the working hours in the controlled zones is 20
> centigride, and the temperature is 20 centigride in the working
> hours , but in some zones the temperature in the nonworking hours is
> above 20 centigrade, especially it is almost 24 centigrade in 1:00
> a.m in a perimeter zone. The building is an office building, and the
> system is only turned on in the working hours. How can I let the
> temperature in the controlled zones in the winter be reasonable?
> Could you help me?
>
> Best,
>
> Stewart
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
------------------------ Yahoo! Groups Sponsor --------------------~-->
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/