[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] question about air-air heat recovery with economizer



Hi,
 
You should try setting the economizer choice to "Bypass" in the Controller:Outside Air object.    I also see these error messages on a routine basis when doing runs where the rest of the system is being autosized.  (e.g. I just did a run that produced a 12 megabyte .err file full of them!).   In my case it is more of an ERV sizing issue than an economizer issue.  Calculation accuracy isn't affected much by having a poorly sized ERV.  But running an ERV during economizing can be expected to seriously degrade the benefits of free cooling  -- hence "bypass".  
 
Brent
 
 -----Original Message-----
From: Chaoqin Zhai [mailto:chaoqinz@xxxxxxxxxxxxxx]
Sent: Thursday, November 04, 2004 12:46 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] question about air-air heat recovery with economizer



Hi,

I have an air-air total heat recovery in the system. In addition, I set the 
system could go into economizer mode when the outdoor condition is within a 
certain limit. When I ran the simulation using EnergyPlus, an error message 
is generated, which said: HEAT EXCHANGER:AIR TO AIR:GENERIC "ERV" average 
air volume flow rate is <50% or >130% of the nominal HX supply air volume 
flow rate.

To my understanding it is because the outside air flow rate is getting 
higher than the minimum outside air flow rate, which is the same as nominal 
air flow rate of the ERV, when the system is in economizer mode. Am I 
right? Will this warning affect the calculation accuracy of the simulation?

Thanks a lot!


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.




Yahoo! Groups Sponsor	

ADVERTISEMENT
 <http://us.ard.yahoo.com/SIG=12920g2vj/M=315388.5543473.6613715.3001176/D=groups/S=1705007389:HM/EXP=1099683876/A=2372354/R=0/SIG=12id813k2/*https://www.orchardbank.com/hcs/hcsapplication?pf=PLApply&media=EMYHNL40F21004SS> click here	
  <http://us.adserver.yahoo.com/l?M=315388.5543473.6613715.3001176/D=groups/S=:HM/A=2372354/rand=472346834> 	


  _____  

Yahoo! Groups Links


*	To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
  

*	To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe> 
  

*	Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service <http://docs.yahoo.com/info/terms/> . 




[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
Make a clean sweep of pop-up ads. Yahoo! Companion Toolbar.
Now with Pop-Up Blocker. Get it for free!
http://us.click.yahoo.com/L5YrjA/eSIIAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/