Re: [EnergyPlus_Support] question about air-air heat recovery with economizer




Economizer choice for Controller:Outside Air should be set to "Bypass" 
when heat recovery is used.  See Heat Exchanger:Air To Air:Generic in 
the IO Reference Manual for further details.

Chaoqin Zhai wrote:

> Hi,
>
> I have an air-air total heat recovery in the system. In addition, I 
> set the
> system could go into economizer mode when the outdoor condition is 
> within a
> certain limit. When I ran the simulation using EnergyPlus, an error 
> message
> is generated, which said: HEAT EXCHANGER:AIR TO AIR:GENERIC "ERV" average
> air volume flow rate is <50% or >130% of the nominal HX supply air volume
> flow rate.
>
> To my understanding it is because the outside air flow rate is getting
> higher than the minimum outside air flow rate, which is the same as 
> nominal
> air flow rate of the ERV, when the system is in economizer mode. Am I
> right? Will this warning affect the calculation accuracy of the 
> simulation?
>
> Thanks a lot!
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the 
> appropriate folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
> <http://us.ard.yahoo.com/SIG=12920g2vj/M=315388.5543473.6613715.3001176/D=groups/S=1705007389:HM/EXP=1099683876/A=2372354/R=0/SIG=12id813k2/*https://www.orchardbank.com/hcs/hcsapplication?pf=PLApply&media=EMYHNL40F21004SS> 
>
>
>
> ------------------------------------------------------------------------
> Yahoo! Groups Links
>
>     * To visit your group on the web, go to:
>       http://groups.yahoo.com/group/EnergyPlus_Support/
>        
>     * To unsubscribe from this group, send an email to:
>       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>        
>     * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>       Service <http://docs.yahoo.com/info/terms/>.
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/