Re: [EnergyPlus_Support] Electricity:Plan Problem



In the mtd output file, ~LG test20 singlepump 01.mtd, there is a section which 
lists all of the components on each meter

 For Meter=Electricity:Plant [J], contents are:
  CHILLER3(SYS_2):Chiller Electric Consumption
  CHILLER4(SYS_2):Chiller Electric Consumption
  CHILLER5(SYS_2):Chiller Electric Consumption
  CHILLER6(SYS_2):Chiller Electric Consumption
  HW CIRC PUMP:Pump Electric Consumption
  CWP4(SYS_2):Pump Electric Consumption

This tells you that chillers and pumps are on the Electricity:Plant meter.  
Create a report variable command for each of these and redo the run.  For 
example:

Report Variable,
    *,                       !- Key_Value
    Chiller Electric Consumption,    !- Variable_Name
    hourly;                  !- Reporting_Frequency

Report Variable,
    *,                       !- Key_Value
    Pump Electric Consumption,    !- Variable_Name
    hourly;                  !- Reporting_Frequency

My guess is that you will find that one or both of the pumps is running all the 
time.

Mike


On 11 Nov 2004, at 22:31, wing sun lee wrote:

> 
> Hi,
> 
> Sorry, I don't know how to do it. Would you mind teaching me or highlight which
> part is faulty.
> 
> Regards,
> 
> SAMLEE
> 
> 
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> Have you reported every variable that is part of Electricity:Plant?  Which ones
> are consuming power?
> 
> You cannot draw all of your system in HVAC diagram in a single run due to a
> suspected bug in HVAC diagram.  To get a drawing of all of the fancoil units,
> delete all AIR PRIMARY LOOPs and associated components and re-run.  All of the
> fan coil system should draw.  
> 
> Mike
> 
> On 9 Nov 2004, at 1:15, wing sun lee wrote:
> 
> > 
> > Hi
> > 
> > Based on your previous comments for the Electricity:Plan, I have checked the
> > schedule for the chillers and pumps. All schedules seem to be corrected. Could
> > you please help me to check that.
> > 
> > Beside, for the HVAC diagram, I still don't understanding how to display the
> > rest of the FCUs objects.
> > 
> > Please help me.
> > 
> > SAMLEE
> > 
> > Encl.
> > 
> > 
> > 
> > ­É¹L¡B¤@©ç¨â´²¡B©_¬¥§õºû´µ¦^«H...
> > ¥þ´ä³Ì¤j¤â¾÷¤U¸ü¤¤¤ß
> > http://mobile.yahoo.com.hk/
> > 
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> 
> 
> Yahoo! Groups Sponsor 
> Get unlimited calls to
> 
> U.S./Canada
> 
> 
> ---------------------------------
> Yahoo! Groups Links
> 
>    To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>    To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> 
> 
> ­É¹L¡B¤@©ç¨â´²¡B©_¬¥§õºû´µ¦^«H...
> ¥þ´ä³Ì¤j¤â¾÷¤U¸ü¤¤¤ß
> http://mobile.yahoo.com.hk/
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/