[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Air primary loop has no air flow?????





There is another problem.When i don't set condenser loop temp 
setpoint,there will be a warning.But i found that in the example 
itself,it doesn't set it yet and there is no warning.why???

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "hbn_pch" <hbn_pch@y...> 
wrote:
> 
> Hi,
>   Thank you very much,Mike.According to your hint,i modify the 
> example and the previous problem is cleared away.However,it appear 
> new warnings,which are all the same:
> 
> ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
> Loop=HEATING LOOP, Outlet and Inlet differ by more than tolerance.
>    **   ~~~   ** Loop inlet node=HP INLET, 
> flowrate=1.142157060549204E-002
>    **   ~~~   ** Loop outlet node=PS_H_OP_OUTLET, 
> flowrate=2.284314121098408E-002
> 
> ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
> Loop=HEATING LOOP -- continues ** 500
>    ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
> Loop=HEATING LOOP -- continues ** 1000
>    ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
> Loop=COOLING LOOP -- continues ** 1500
>    ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
> Loop=COOLING LOOP -- continues ** 2000
>    ** Warning ** Error -- Mass Flow Rate Calculation in Plant 
> Loop=COOLING LOOP -- continues ** 2500
> 
> ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC 
> loops, at SUMMER DESIGN, 07/21 08:36 - 08:37
>    ** Warning ** SimHVAC: Maximum iterations exceeded for all HVAC 
> loops, at SUMMER DESIGN, 07/21 08:37 - 08:38
> 
>   Expect your kind reply,thanks!
> 
> 
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
> <mjwitte@g...> wrote:
> > In the <Zone Sizing Information> report in the eio output file, 
all 
> of the zone 
> > design loads are zero.  This usually indicates a problem with the 
> thermostat 
> > inputs.  The Zone_control_type_day schedule is incorrect.  It it 
> always 0.044, 
> > which is interpreted as zero which means no heating or cooling is 
> active.  This 
> > schedule should only contain integer values from 0 to 4.  See the 
> section about 
> > Zone Control:Thermostatic in the Input Output Reference (p. 659, 
> pdf p. 689) 
> > for an explanation of the thermostat control type schedule.  
> > 
> > Mike
> > 
> > On 29 Nov 2004, at 2:38, hbn_pch wrote:
> > 
> > > 
> > > 
> > > Hi,
> > >   i just simulate a story buinding.But it tells me that the air 
> > > primary loop has no air flow???Why???
> > >   Is the loop connection false???I've uploaded my idf.
> > > 
> > >   Thanks for all your kind help!!!!! 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > > 
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > > 
> > > Attachments are not allowed -- please post any files to the 
> appropriate folder
> > > in the Files area of the Support Web Site.
> > > 
> > > Yahoo! Groups Links
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > > 
> > 
> > 
> > 
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support      
> > EnergyPlus-Support@g...





------------------------ Yahoo! Groups Sponsor --------------------~--> 
$9.95 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/J8kdrA/y20IAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/