[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: zone load calculation?





Hi,
  Thanks.
  I don't understand specifying temperature controls.Does it mean 
that i should specify zone control:thermostic?I'am puzzled.
  Take 5ZoneEngChill.idf for a example:single heating setpoint is 12.8
(1am-7am and 6pm-12pm) and 21.1(7am-6pm);single cooling setpoint is 40
(1am-7am and 6pm-12pm) and 23.9(7am-6pm).I don't understand these 
temperature values.Does these values describe the temp demand of user?
How can i get the real temperature of the thermostic?I guess zone/sys 
air temp describe this values(Is it right?).Meanwhile,i found the 
lower temp of the single cooling setpoint(23.9) should be bigger than 
the upper temp of the single heating setpoint(21.1),if not ,there is 
warning.
  problem 2:The supply air temperature is 16(while heating) and 12.8 
(while cooling).I don't know how can these two temperature can 
maintain the zone temperature in 21(heating) and 23.9(cooling)?For 
example ,the zone temp is 14 and the supply air temp is 16(vav 
outlet),how can the zone temp rise to 21?i'am puzzled.At least,the 
supply air temp should >21?
  problem 3:Last time,i ask the problem of the zone/sys sensible 
heating/cooling rate.Mike tells me,when zone temp(temp of thermostic)
>16,report cooling;<16 heating.It occurs while the vav system is 
off.But when vav system is on,what values should i take to compare 
with? 
  problem 4:If i specify the temperature control and the HVAC.I want 
to get zone load.Do the zone/sys sensible heating/cooling can 
represent it? 
  problem 5:following is my understand for the three temp,right???
zone thermostat setpoint:describe temp demand of the user.
zone temperatures:the temp of the thermostic
system supply air temperature:vav system outlet temp,is fixed at 16
(heating) and 12.8(cooling).

  I'm ablush for asking so many questions.But appreciated your kind 
help.Thanks.
  Bless to you!
  pch




--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@g...> wrote:
> In order to determine heating and cooling loads in EnergyPlus, you 
need to 
> specify temperature controls and some type of HVAC system.  The 
simplest system 
> is "purchased air" which is an infinite supply of hot and cold 
air.  This can 
> be used to calculate loads without specifying a full HVAC system.  
There is a 
> sample file called "PurchAir.idf" in the EnergyPlus\ExampleFiles 
folder which 
> will show you the objects required.
> 
> However, it is critical that users understand the limitations of 
the PURCHASED 
> AIR model.  The description of the model and its outputs beings on 
p. 520 of 
> the Input Output Reference (pdf p. 548, version 1.2.0). 
> 
> Mike
> 
> On 2 Dec 2004, at 12:17, hbn_pch wrote:
> 
> > 
> > 
> > Dear,
> >   I meet a new problem.For a long time,i calculate zone load with 
the 
> > sum of the Zone-Total Internal Radiant Heat Gain,Zone-Total 
Internal 
> > Convective Heat Gain,Zone-Total Internal Visible Heat Gain,Zone-
Total 
> > Internal Latent Gain and Zone-Total Internal Radiant Heat 
> > Gain.Today,i found these values are just the internal load,such 
as 
> > people,lights and equipments(Is it right?).
> >   Then a problem come in,how can i calculate the zone load?In 
other 
> > words,what report variables should i add in the report variable 
> > object to calculate the zone load???
> >   Another problem,in the .eio<Zone Sizing Information>,the 
cooling 
> > and heating load is the load in the design day(Is it right?).Are 
> > these two load values calculated in the worst condition?Are they 
> > biggest?
> >   I'am a newbie in this field,appreciated to your kind help.Thanks
> > 
> >   pch 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the 
appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@g...





------------------------ Yahoo! Groups Sponsor --------------------~--> 
$4.98 domain names from Yahoo!. Register anything.
http://us.click.yahoo.com/Q7_YsB/neXJAA/yQLSAA/dkFolB/TM
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/