Re: [EnergyPlus_Support] Help!
It seems that the last coil in your system is being "starved" with inadequate water flow rate.
Some reasons i can possibly anticipate this is:
Supply side Max Chilled Water Flow rate should be increased. Because that flow goes to each of your 8 coils in sequence and is able to satisfy only the first 7 coils ie runs out of flow on reaching the 8th coil. Basically try to increase the capacity of your system.
Try adjusting the controller max flow rate.
Check your Coil Schedule also, coil could be possibly scheduled off.
hope this helps
Rahul Chillar
zyyh9819 <zyyh9819@xxxxxxxxxxxx> wrote:
Thank you very much for your reply!
But I have another question. There are eight cooling coil in my
idf, and each cooling coil belong to one Air Primary Loop.
In the result of my simulation, I find the Water MassFlowRate
through one of the cooling coil is zero at any time,so the Mean Air
Temperature in one zone is too high. The other cooling coil and Loop
works well. I can not explain it. Can you give me a hint? Thanks a
lot!
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
---------------------------------
Yahoo! Groups Links
To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service.
---------------------------------
Do you Yahoo!?
Read only the mail you want - Yahoo! Mail SpamGuard.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/