Radiant system will impact window heat loss/gain primarily by altering the
inside surface temperature due to radiant exchange with the warm/cool radiant
surface. Report the inside and outside surface temperatures for both cases.
Are you comparing the total gain/loss for a whole year, design day, or a
particular hour?
Mike
On 4 Jan 2005, at 18:55, pizzaalan wrote:
> I have a question on window heat loss & gain for different systems.
> I checked the two example files, ¡°VAVSingleDuctReheatBaseboard¡±
> and ¡°RadLoTempCFloHeatCool¡±. I found that both the window heat
> loss and gain of the Radiant system are 10 times higher than that of
> the VAV system, although the building construction and location are
> same. This could be only due to net IR heat flow to the zone from
> the glazing, is it right? I also simulated a building using those
> two systems; I found that the window heat loss and gain of my
> Radiant system are 100 times higher than that of my VAV system,
> which is obviously wrong. Is there anyway to check how Energy+
> calculates the window heat loss and gain? What input parameter could
> affect the calculation of the window heat loss and gain?
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/