Re: [EnergyPlus_Support] Re: Help!
As "pch" said, the radiant system needs to be listed in a ZONE EQUIPMENT LIST
which must be referenced in a CONTROLLED ZONE EQUIP CONFIGURATION object. And
there is no no need for a controller list for this type of system. See
ExampleFiles\RadLoTempElecTermReheat.idf for an example.
Mike
On 7 Jan 2005, at 7:17, hbn_pch wrote:
>
>
> Dear shirely213,
> You have lost two input:'Zone Equipment' List and 'Controlled Zone
> Equipment Configuration'.It cause the warning.
> Otherwise,i find your building materials is Material:Regular-
> R,there is no thermal mass .Advise you to use Material:regular
>
> pch
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "shirely213"
> <shirley213213@1...> wrote:
> >
> > Dear all
> > I simulate a building with an electric heating system¡ª¡ªRadiant
> > Panel. I control the heating system by¡°Radiative / Conventive
> > Units¡± and ¡°Zone Controls and Thermostats¡±.But the simulated
> > result of the building¡¯s energy consumption is ¡°Zero¡± all the
> > time .
> > In the ERR file, it says:
> > The following lines are "Orphan Objects". These objects are in the
> > idf file but are never obtained by the simulation and therefore are
> > NOT used.
> > ** ~~~ ** See InputOutputReference document for more details.
> > ************* Object=CONTROLLER LIST=RADIANT PANEL CONTROLLER
> > ************* Object=LOW TEMP RADIANT SYSTEM:ELECTRIC=RADIANTPANEL
> > Looking forward to your help!
> > Thanks a lot!
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/