Re: [EnergyPlus_Support] about node temperatures




If the pump power remains constant and the flow varies, low flows will get hot 
because the energy must go somewhere.  You either need to let the pump power 
vary (linear power would use coefficients of 0,1,0,0) or use a constant speed 
pump so the excess flow will go through the bypass.

Mike

On 14 Jan 2005, at 16:39, zhen tian wrote:

> 
> Hi, Mike:
> 
> Thanks for you reply. I have checked the pump input. Actually, I do use variable
> flow pumps with constant pump power.  But I cannot change rated pump power
> consumption to "autosize" as this will cause severe errors. I did not use any
> autosize function in my model.  I have upload my model named " ICT-NoRC-zt.zip "
> to the yahoo group. Could you check it for me? Thanks a lot. The weather file is
> Calgary, Alberta.
> 
> Regards,
> 
> Zhen 
> "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> My guess is that there is something wrong with the pump inputs.  Is this a
> variable flow system with constant pump power?  Look at the pump inlet and
> outlet temperatures, flow rate and pump electric power consumption.  This my
> reveal the problem.
> 
> Mike
> 
> 
> On 13 Jan 2005, at 16:09, zhen tian wrote:
> 
> > 
> > 
> > Hi everyone:
> > 
> > I am simulating a building with five zones serviced by a VAV system. I set up
> > the heating plant (purchased heating) temperature as 93 degree C.  The
> > simulation goes through well, but when I check the system node temperature, I
> > found that the "HW SUPPLY OUTLET NODE:System Node Temp[C](Hourly)" the
> > temperature sometimes are " 93, 93, 111.1, 1111.4, 93.2, 93.2, 3533.6...."
> > 
> > And even the "CW PUMP OUTLET NODE:System Node Temp[C](Hourly) " is like this:
> > " 1369.2, 2723.5, 11.7, 10.8, 1783.1..."
> > 
> > when I run the simulation in a typical summer day.
> > 
> > Could somebody tell me what is the problem?
> > 
> > Regards,
> > 
> > Zhen
> > 
> > 
> > 
> > 
> > ---------------------------------
> > Do you Yahoo!?
> >  Yahoo! Mail - now with 250MB free storage. Learn more.
> > 
> > [Non-text portions of this message have been removed]
> > 
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> 
> 
> Yahoo! Groups SponsorADVERTISEMENT
> document.write('');
> 
> ---------------------------------
> Yahoo! Groups Links
> 
>    To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>    To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>    Your use of Yahoo! Groups is subject to the Yahoo! Terms of Service. 
> 
> 
> 
> ---------------------------------
> Do you Yahoo!?
>  Take Yahoo! Mail with you! Get it on your mobile phone.
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 






The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/