Zone/Sys Sensible Load Predicted is the required heating/cooling to satisfy the
thermostat, Zone/Sys Sensible Heating Rate is the actual amount of heating
delivered to the zone by the system. If the system does not have adequate
capacity, Zone/Sys Sensible Heating Rate will be less than Zone/Sys Sensible
Load Predicted and the zone temperature will fall. Then in the next time step,
Zone/Sys Sensible Load Predicted will be greater because it will include the
entire load required to meet the thermostat (including the unmet load from the
previous time step). So, Zone/Sys Sensible Heating Rate is the better choise.
Mike
On 28 Jan 2005, at 15:59, ping sun wrote:
>
> hi,
> I want to ask a question about heating and cooling load.
> If I want to caculate the load ,what should I write in report variable? what
> is the difference between Zone/Sys Sensible Heating Rate and Zone/Sys
> Sensible Load Predicted?
>
>
>
>
> ---------------------------------
> Do You Yahoo!?
> ×¢²áÊÀ½çÒ»Á÷Æ·ÖʵÄÑÅ»¢Ãâ·ÑµçÓÊ
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/