BRANCHes are only a way to connect components together.  Every component listed 
on a BRANCH must exist elsewhere in the idf file.  In this case the first error 
message indicates that it could not find a PIPE object with the name 
"INLETSIDE".  

However, for your system, you do not need any PIPE objects.  The branch for the 
air loop should contain things such as a fan and coils and possibly an outside 
air system.  For an example of a simulation with low temp electric radiant 
heat, see RadLoTempElecTermReheat.idf

Mike


On 28 Jan 2005, at 7:51, shirely213 wrote:

> 
> 
> Dear all:
> 
>   AirLoop Main Branch1                  AirLoopMain Branch2
> 3                      1 RadiantPanel 2                     4
> Node List:
> 1£ºEQUIPINLETNODE
> 2£ºEQUIPOUTLETNODE
> 3£ºZONE1OUTLETNODE
> 4£ºZONE1INLETNODE
>   My system¡¯s sketch map is above. It is a radiant panel system 
> without outside air. Now ,in my idf file ,there are some errors in my 
> BRANCH ,the ERR says: 
> ** Severe  ** During Branch Input, Invalid Component Name 
> input=INLETSIDE
>    **   ~~~   ** Component type=PIPE
>    **   ~~~   ** Occurs on Branch=AIR LOOP MAIN BRANCH1
>    ** Severe  ** During Branch Input, Invalid Component Name 
> input=OUTLETSIDE
>    **   ~~~   ** Component type=PIPE
>    **   ~~~   ** Occurs on Branch=AIR LOOP MAIN BRANCH2
>   The Component Name is just asked to be unique in the
> ¡°InputOutputReference.pdf¡±. Why is it invalid? And thanks for 
> checking my BRANCH and LOOP, I am not very sure if it is right. Is my 
> system¡¯s sketch map is in reason? 
> 
>   The Branch compenent should be FANS¡¢CIOLS or others. In my 
> system ,there is just a radiant panel ,must I have some BRANCHES?
> 
>   Can you give me some advices on the AIRLOOP of my system?
> 
>   I have sent on my .idf file .
> 
>   Thanks a lot !
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/