[EnergyPlus_Support] Re: Two equipments in serie in a water loop
Severe ** Error Detected in Branch List=HEATING SUPPLY SIDE BRANCHES
** ~~~ ** Actual Error occurs in Branch=HEATING SUPPLY OUTLET
BRANCH
** ~~~ ** Branch Outlet does not match Inlet, Outlet=OUTLET
SECOND BOILER
** ~~~ ** Inlet Name=HEATING SUPPLY EXIT PIPE INLET NODE
For some reason E+ is considering as branch outlet the outlet of the
first equipment and as branch inlet the inlet of the second equipment
in the branch ???? ( I mean first and second equipment according to
flow direction )Anyway I solved the problem by eliminating
the "supply exit pipe" I have the two boilers up and running now, I
still have a problem with the second boiler that goes on when it
should not.
Thanks again.
Andrea.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
<mjwitte@g...> wrote:
> There is an example file TRHConstFlowChillerOneBranch.idf which has
a single
> branch for the chilled water supply side with a pump and chiller on
the same
> branch. What kind of problems are occuring?
>
> Mike
>
>
> On 1 Feb 2005, at 15:00, ingdallolio wrote:
>
> > Two equipments in serie in a water loop, should be simple but I
> > can't make it work !? is there any example file that shows it ?
Has
> > anybody never run an IDF file with that kind of thing ?
> > Just as a test I'm using two pipes.
>
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@g...
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/