Re: [EnergyPlus_Support] Re: Two equipments in serie in a water loop
When listing components on a branch, the outlet node from component one must be
the same node name as the inlet node of component two. I am fairly certain
that this error message indicates that this is not true for that branch.
Mike
On 4 Feb 2005, at 14:53, ingdallolio wrote:
>
>
> Severe ** Error Detected in Branch List=HEATING SUPPLY SIDE BRANCHES
> ** ~~~ ** Actual Error occurs in Branch=HEATING SUPPLY OUTLET
> BRANCH
> ** ~~~ ** Branch Outlet does not match Inlet, Outlet=OUTLET
> SECOND BOILER
> ** ~~~ ** Inlet Name=HEATING SUPPLY EXIT PIPE INLET NODE
>
> For some reason E+ is considering as branch outlet the outlet of the
> first equipment and as branch inlet the inlet of the second equipment
> in the branch ???? ( I mean first and second equipment according to
> flow direction )Anyway I solved the problem by eliminating
> the "supply exit pipe" I have the two boilers up and running now, I
> still have a problem with the second boiler that goes on when it
> should not.
> Thanks again.
> Andrea.
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@g...> wrote:
> > There is an example file TRHConstFlowChillerOneBranch.idf which has
> a single
> > branch for the chilled water supply side with a pump and chiller on
> the same
> > branch. What kind of problems are occuring?
> >
> > Mike
> >
> >
> > On 1 Feb 2005, at 15:00, ingdallolio wrote:
> >
> > > Two equipments in serie in a water loop, should be simple but I
> > > can't make it work !? is there any example file that shows it ?
> Has
> > > anybody never run an IDF file with that kind of thing ?
> > > Just as a test I'm using two pipes.
> >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@g...
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/