Re: [EnergyPlus_Support] Solar Heating System




The current water heater model can be a bit difficult to work with.  I would 
suggest putting the boiler in parallel with the water heater rather than in 
series.  I know the real system would put them in series, but for the 
simulation the energy use should be equivalent.  This way the mass flow does 
not have to be the same in both components which may be why you are having 
trouble with them.

Sorry about the slow response.

Mike


On 3 Feb 2005, at 12:35, ingdallolio wrote:

> 
> 
> I'm modeling a solar collector heating system with low temperature 
> radiant floor.
> I'm using a water heater object to exchange heat from the collector 
> loop to the radiant floor water loop. I'd like to run with both solar 
> energy and gas (as backup energy source). The gas burner should start 
> when the temperature on the second loop ( radiant floor ) goes below 
> 30C. If I set the water heater set point to 30C the temperature 
> inside the water heater tank ( collector loop) does not go above 
> 30C !. I'd like the water heater storage temperature to go as high as 
> possible, in order to storage as much solar energy as possible. I was 
> thinking to use two heater ( a water heater and a boiler objects) in 
> series but I can't make this working.
> Any idea?
> Thanks, Andrea.  
> 
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/