Re: [EnergyPlus_Support] 100% Outside




There's the Ventilation object. It includes fan energy consumption

Fred

Edward Lyon wrote:

>back to the jms_dtz issue
> 
>So the system could be modeled using infiltration to provide the 100%
>outside air to the individual zones based on the occupancy schedule, but
>if you wanted the fan energy as well you would have to create a dummy
>zone with a primary air volume equal to and operating when the
>ventilation infiltration is active for the rest of the building....
> 
>Ned
>
>________________________________
>
>From: Michael J. Witte [mailto:mjwitte@xxxxxxxx] 
>Sent: Thursday, February 10, 2005 3:43 PM
>To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>Subject: RE: [EnergyPlus_Support] 100% Outside
>
>
>The limitation in the current software is that there can only be one
>return 
>node per zone.  So, a zone can be served by multiple systems, but only
>one of 
>those systems can be an air loop with a return path.  The other
>system(s) must 
>be zone equipment (not on an AIR PRIMARY LOOP) which uses supply and
>exhaust 
>nodes.  The reason for this is that the current structure does not have 
>adequate information to determine how to divide the total return flow
>from a 
>zone among multiple return air nodes.
>
>Mike
>
>
>On 8 Feb 2005, at 16:14, Edward Lyon wrote:
>
>  
>
>>So if the structure of the program wants a return, why not provide one
>>    
>>
>for your
>  
>
>>outside airflow study?  The return can go to a mixing box set for 100%
>>    
>>
>exhaust. 
>  
>
>>I don't think you have to have an energy penalty for the return duct
>>    
>>
>flow.
>  
>
>>In the distant future when COMIS and mechanical systems can be
>>    
>>
>combined, it
>  
>
>>might be nice to just supply air to a space and have it return/exhaust
>>    
>>
>where it
>  
>
>>finds a place.  I think the bigger problem that should have more
>>    
>>
>development
>  
>
>>attention now is modeling a common mechanical system design with
>>    
>>
>several
>  
>
>>supplies to different spaces (zones), but only one common return point
>>    
>>
>(zone). 
>  
>
>>This is a typical small house or apartment system where supply from
>>    
>>
>one zone
>  
>
>>must flow through a second (third or fourth sometimes) zone to get to
>>    
>>
>the
>  
>
>>return.  Mixing and cross mixing doesn't really do the job to simulate
>>    
>>
>this
>  
>
>>design.  We might have more efficient small house designs if we could
>>    
>>
>study this
>  
>
>>system to determine better zone flow balances or thermostat
>>    
>>
>placement.... 
>  
>
>>Ned Lyon, Senior Project Manager
>>
>>Simpson Gumpertz & Heger Inc.
>>41 Seyon Street, Bldg 1 Suite 500
>>Waltham, Massachusetts  02453
>>
>>781-907-9350
>>
>>________________________________
>>
>>From: fred buhl [mailto:wfbuhl@xxxxxxx]
>>Sent: Tue 2/8/2005 1:56 PM
>>To: EnergyPlus_Support@xxxxxxxxxxxxxxx
>>Subject: Re: [EnergyPlus_Support] 100% Outside
>>
>>
>>I'm pretty sure this doesn't work right now - although it should. I 
>>tried it fairly recently
>>and was unsuccessful. You may have to resort to zone equipment of some
>>    
>>
>
>  
>
>>sort. This is
>>a serious defficiency which we simply haven't had the time/people to 
>>address.
>>
>>Fred Buhl
>>
>>jms_dtz wrote:
>>
>>    
>>
>>>Has anyone modeled a 100% outside air system?  I'm trying to provide 
>>>assisted ventilation to a vav system based on occupancy.  I've set it
>>>      
>>>
>
>  
>
>>>up to use direct air to the zones off a second air loop, but I want 
>>>to supply outside air without a zone return, and I'm having trouble 
>>>setting up the nodes.  Any ideas?
>>>
>>>
>>>
>>>
>>>
>>>The primary EnergyPlus web site is found at:
>>>http://www.energyplus.gov
>>>
>>>The group web site is:
>>>http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>>Attachments are not allowed -- please post any files to the
>>>      
>>>
>appropriate folder
>  
>
>>>in the Files area of the Support Web Site.
>>>
>>>Yahoo! Groups Links
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> 
>>>
>>>      
>>>
>>The primary EnergyPlus web site is found at:
>>http://www.energyplus.gov
>>
>>The group web site is:
>>http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>>Attachments are not allowed -- please post any files to the
>>    
>>
>appropriate folder
>  
>
>>in the Files area of the Support Web Site.
>>
>>
>>
>>
>>Yahoo! Groups Sponsor      
>>ADVERTISEMENT
>>
>>
>>    
>>
><http://us.ard.yahoo.com/SIG=129pslgo8/M=298184.6018725.7038619.3001176/
>D=group
>  
>
>s/S=1705007389:HM/EXP=1107974068/A=2532114/R=2/SIG=12ki81kc1/*http://clk
>.atdmt.
>  
>
>> com/NFX/go/yhxxxnfx0020000014nfx/direct/01/&time=1107887668146011> 
>>
>>
>>________________________________
>>
>>Yahoo! Groups Links
>>
>>
>>*      To visit your group on the web, go to:
>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>>*      To unsubscribe from this group, send an email to:
>> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>>
>>    
>>
><mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
>be> 
>  
>
>>*      Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>>    
>>
>Service
>  
>
>><http://docs.yahoo.com/info/terms/> . 
>>
>>
>>
>>
>>[Non-text portions of this message have been removed]
>>
>>
>>
>>The primary EnergyPlus web site is found at:
>>http://www.energyplus.gov
>>
>>The group web site is:
>>http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>>Attachments are not allowed -- please post any files to the
>>    
>>
>appropriate folder
>  
>
>>in the Files area of the Support Web Site.
>>
>>Yahoo! Groups Links
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>    
>>
>
>
>
>========================================================
>Michael J. Witte, GARD Analytics, Inc.
>EnergyPlus Testing and Support      
>EnergyPlus-Support@xxxxxxxx
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate
>folder in the Files area of the Support Web Site.
>
>
>
>
>Yahoo! Groups Sponsor	
>ADVERTISEMENT
>
> 
><http://us.ard.yahoo.com/SIG=129b8h1lc/M=298184.6018725.7038619.3001176/
>D=groups/S=1705007389:HM/EXP=1108155726/A=2532114/R=2/SIG=12kt5qhqq/*htt
>p://clk.atdmt.com/NFX/go/yhxxxnfx0020000014nfx/direct/01/&time=110806932
>6437675> 
> 
><http://us.adserver.yahoo.com/l?M=298184.6018725.7038619.3001176/D=group
>s/S=:HM/A=2532114/rand=431887938> 	
>
>________________________________
>
>Yahoo! Groups Links
>
>
>*	To visit your group on the web, go to:
>	http://groups.yahoo.com/group/EnergyPlus_Support/
>	  
>*	To unsubscribe from this group, send an email to:
>	EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
><mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
>be> 
>	  
>*	Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>Service <http://docs.yahoo.com/info/terms/> . 
>
>
>
>
>[Non-text portions of this message have been removed]
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>
>
>  
>


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/