Re: [EnergyPlus_Support] Re: the condenser fan energy for air-cooled chiller




Add these report variables to your input file (IDF file) to see their 
values:

Chiller Electric Consumption
Tower Fan Electric Consumption

example:
  Report Variable,
    *,                       !- Key_Value
    Chiller Electric Consumption,  !- Variable_Name
    timestep;                !- Reporting_Frequency

  Report Variable,
    *,                       !- Key_Value
    Tower Fan Electric Consumption,  !- Variable_Name
    timestep;                !- Reporting_Frequency

See Report Variables on pg. 926 of the IO Reference Manual for further 
details.

These outputs are already included on the meters Electricity:Plant and 
Cooling:Electricity.

See Report Meter on pg. 928 of the IO Reference Manual for further details.

beyangj wrote:

>
> Dear,
> Thanks again for your reply. Now I know the condenser fan electric
> consumption is included on the meters Electricity:Plant and
> Cooling:Electricity.When I set the condenser fan power ratio greater
> than 0, I can get Chiller Electric Consumption and Chiller Cond Fan
> Electric Consumption from the report variable of Electricity:HVAC or
> Electricity:Plant. I wonder how can I get the Chiller Electric
> Consumption and Chiller Cond Fan Electric Consumption, respectively.
> How can I specify the report varibles for these two varibles in the
> item of Report MeterFileOnly in the IDF file?
>
> Sincerely,
>
> Stewart
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
> <RRaustad@F...> wrote:
> > Check manufacturers product catalog data for specific chiller
> > information. The condenser fan power ratio (Fan Power [W] /
> Nominal
> > Capacity [W]) varies among different chiller types, chiller sizes,
> and
> > fan selection.  Use 0.01 to get you started.
> >
> > beyangj wrote:
> >
> > >
> > > Dear,
> > > Thank you very much for your reply, your advice is very helpful.
> Now
> > > I still have a question, namely, which is the proper value of the
> > > condenser fan power ratio?
> > >
> > > Best,
> > >
> > > Stewart
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "donbshireyiii"
> > > <shirey@f...> wrote:
> > > >
> > > > Adding to the previous response...
> > > >
> > > > As has been noted several times in previous e-mail support
> > > responses,
> > > > look at the meter details file (*.mtd). This file shows what
> report
> > > > variables are on which meters and vice versa -- which meters
> > > contain
> > > > what report variables (see OutputDetailsAndExamples.pdf, page
> 54 of
> > > > the pdf or numbered page 42, item "eplusout.mtd"). If you are
> using
> > > > EP-Launch, push F12 to see the .mtd file for the input data
> file
> > > > (.idf) that you are using.
> > > >
> > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
> > > > <RRaustad@F...> wrote:
> > > > > Check the data dictionary (*.rdd) file for Chiller Cond Fan
> > > > Electric
> > > > > Power and Chiller Cond Fan Electric Consumption. Use these
> > > outputs
> > > > to
> > > > > view the condenser fan power for Chiller:Electric:EIR. They
> will
> > > > only be
> > > > > present in the *.rdd file if the Condenser Fan Power Ratio is
> > > > greater
> > > > > than 0 for the chiller in question. The condenser fan
> electric
> > > > > consumption is included on the meters Electricity:Plant and
> > > > > Cooling:Electricity.
> > > > >
> > > > > beyangj wrote:
> > > > >
> > > > > >
> > > > > >
> > > > > > Dear,
> > > > > > I used the chiller:electric EIR chiller in my model, and
> this
> > > > > > chiller was a air-cooled chiller, and I got the energy
> > > consumption
> > > > > > in the meter.csv file, but I don't know how to get the
> energy
> > > > > > consumption of the condenser fans. I wondered whether the
> > > energy
> > > > > > consumption of the air-cooled chiller in the meter.csv file
> > > > includes
> > > > > > the energy consumption of condenser fans?
> > > > > >
> > > > > > Best,
> > > > > >
> > > > > > Stewart
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> > > appropriate folder in the Files area of the Support Web Site.
> > >
> > >
> > >
> > > Yahoo! Groups Sponsor
> > > ADVERTISEMENT
> > >
> > >
> > > -----------------------------------------------------------------
> -------
> > > Yahoo! Groups Links
> > >
> > >     * To visit your group on the web, go to:
> > >       http://groups.yahoo.com/group/EnergyPlus_Support/
> > >       
> > >     * To unsubscribe from this group, send an email to:
> > >       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> > >       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?
> subject=Unsubscribe>
> > >       
> > >     * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
> > >       Service <http://docs.yahoo.com/info/terms/>.
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL  32922-5703
> > Phone:   (321) 638-1454
> > Fax:     (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
> >
> >
> > [Non-text portions of this message have been removed]
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the 
> appropriate folder in the Files area of the Support Web Site.
>
>
>
> Yahoo! Groups Sponsor
> ADVERTISEMENT
>
>
> ------------------------------------------------------------------------
> Yahoo! Groups Links
>
>     * To visit your group on the web, go to:
>       http://groups.yahoo.com/group/EnergyPlus_Support/
>        
>     * To unsubscribe from this group, send an email to:
>       EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
>       <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>
>        
>     * Your use of Yahoo! Groups is subject to the Yahoo! Terms of
>       Service <http://docs.yahoo.com/info/terms/>.
>
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/