[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: the condenser fan energy for air-cooled chiller





It seems that the fan power is not modulated. I mean, I looking the output data and even if the provided cooling is 1/3 (for example) of the nominal value the fan power is the nominal value. I have to model a chiller that can modulate the fan power. Therefore I'm writing 0 as "condenser fan power ratio" and then I'm modifying the COP in order to take into account the fan power. Then I should check if the curves take into account both the compressor and the fan, but I don't have enough information for that. Any comment, please?

__._,_.___

Posted by: fpasserini.tn@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___