Re: [EnergyPlus_Support] Ventilation:Mechanical object



Air loop/zone connections are reported in the bnd output file.  Search for "Air 
Primary Loops" and review this section of the bnd output file to see a list of 
cooled and heated zones attached to each air loop.  Note that a zone which is 
both heated and cooled is listed only as a cooled zone.  Perhaps the 
information here or in the "Supply Air Paths" section will help diagnose the 
problem.  If not, please submit the input file to the files area in the yahoo 
group or send as a zipped e-mail attachment to energyplus-support@xxxxxxxx

Mike


On 11 Mar 2005, at 20:00, jms_dtz wrote:

> 
> 
> A question about the Ventilation:Mechanical object under the outdoor 
> air controller.  I am using two primary air loops serving seperate 
> zones, and have defined two mechanical ventilation objects.  I keep 
> getting the warning saying,
> "** Warning ** Zone name = DUMMYZN001 in VENTILATION:MECHANICAL 
> object name = ASSIST is not on the same air loop as 
> Controller:Outside air = OACONTROLLER2
>    **   ~~~   ** This zone will not be used and the simulaiton will 
> continue..."
> 
> I've checked and the zone DUMMYZN001 is connected to the same primary 
> air object that OACONTROLLER2 is connected.  This loop happens also 
> to be supplying direct air to the zones it's connected, but that is 
> the only air loop object to those zones.  Is there something about 
> the Ventilation:Mechanical object I'm missing?
> 
> Thanks
> 
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/