Re: [EnergyPlus_Support] About one kind of compressor
A screw chiller is just an electric chiller with a different set of performance
coefficients. The best solution would be to derive performance curve data for
the particular chiller you are modeling. An approximate solution would be to
adjust only the COP and PLR curve data and let the temperature-related curves
stay the same.
Mike
On 14 Mar 2005, at 6:14, energypluser wrote:
>
>
> Dear all,
>
>
> When I am looking the help document, I find that there is no
> module for screw compressor. But I have to do some chiller
> simulation which uses this kind of compressor.
> Could you please give me a suggestion for solving this
> problem?
> Thank you in advance !
>
> Charlie
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/