Re: [EnergyPlus_Support] Re: Thermal mass effect
The radiant ceiling panels certainly complicates matters, because it causes the
surfaces temperatures in the entire zone to be cooler than they would be using
an air-only HVAC system. You mentioned comparing total cooling load. Have you
looked at peak cooling loads? If there is no night venting, then I would
expect thermal mass to have a small impact on total cooling load, but it should
have a significant impact on peak cooling load, essentially flattening out the
swings in cooling load.
Mike
On 6 Apr 2005, at 21:57, sm278424 wrote:
>
>
> Hi Mike,
>
> We've discussed this building before. It has a CV supply air system +
> plenum and radiant ceiling panels.
>
> Answers
> 1. I tried defining all of my constructions as Regular-R to eliminate
> the mass. This increased the total cooling load by just under 5%.
>
> 2. I'm using a combination: furniture and internal partitions are
> internal mass, floors and ceilings are surface objects. Taking out
> the internal mass increased the total cooling load by just about 1%.
>
> 3. ORNL and Berkley Solar Group have done some interesting work here
> on external walls. The location of the concrete (mass) and the
> magnitude of the daily temperature swings are the important factors.
>
> On internal surfaces, I found is that the interaction between the
> radiant ceiling panel and the concrete floor is something to pay
> attention to. Conceivably you could night-cool the building with this
> type of system.
>
> 4. Mostly by tracking the surface tempertures.
>
> Shaun
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte"
> <mjwitte@g...> wrote:
> > I don't have a good reference to offer, but I have some questions
> to ask:
> >
> > 1. The obvious question - are you using Material:Regular so that
> there is
> > actually mass present in the building?
> >
> > 2. Have interior surfaces been described using internal mass or
> surface
> > objects?
> >
> > 3. In a "fully conditioned" building, mass effects tend to be
> small, because
> > most of the mass is not changing temperature very much except
> during
> > transitions to/from thermostat setback. This is especially true if
> the
> > building has a fairly large footprint and a large core to perimeter
> ratio.
> >
> > 4. How are you quantifying the "thermal mass effect"?
> >
> > Mike
> >
> >
> > On 1 Apr 2005, at 17:47, sm278424 wrote:
> >
> > >
> > >
> > > In models I've been working with recently (of a fully air
> conditioned
> > > office building), the thermal mass effect seems quite small.
> > >
> > > Can anyone suggest a good reference on this topic?
> > >
> > > Thanks
> > > Shaun
> > >
> > >
> > >
> > >
> > >
> > > The primary EnergyPlus web site is found at:
> > > http://www.energyplus.gov
> > >
> > > The group web site is:
> > > http://groups.yahoo.com/group/EnergyPlus_Support/
> > >
> > > Attachments are not allowed -- please post any files to the
> appropriate folder
> > > in the Files area of the Support Web Site.
> > >
> > > Yahoo! Groups Links
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> >
> >
> >
> > ========================================================
> > Michael J. Witte, GARD Analytics, Inc.
> > EnergyPlus Testing and Support
> > EnergyPlus-Support@g...
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/