Re: [EnergyPlus_Support] How to model an air cooled heat pump?



A possible solution would be to use HEATPUMP:WATERTOWATER COOLING and 
HEATPUMP:WATERTOWATER HEATING (see example files GSHP-GLHE.idf and 
PlateHeatExchanger.idf).  The source side of the heat pumps would be placed on 
the demand side of a PLANT LOOP.  Set up this plant loop with dual setpoints 
and supply it with PURCHASED:CHILLED WATER and PURCHASED:HOT WATER 
(5ZoneWaterLoopHeatPump.idf) and set the setpoints to be schedules which track 
the outdoor dry bulb temperature +/- a small amount.  You could read in the 
schedules using SCHEDULE:FILE:COMMA. This is rather messy and difficult to set 
up, and I am not completely sure it will work.

On 3 May 2005, at 11:38, Pedro Rodrigo wrote:

> Thanks Michael.
> The heat pump has two operating modes: one for cooling
> water, one for heating water. This conditioned water
> is only used for space heating and cooling through
> several two-pipe terminal units such as Air Handler
> Units and Fan-Coils.
> The heat-pump transfers heat between outside air and
> the water loop.
> I hope this information was what you asked for.
> Looking forward to hearing from you,
> Regards,
> Pedro
> 
> --- "Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
> ---------------------------------
> A heat pump water heater model, based on the DOE-2.1E
> model, is scheduled to be 
> in the Fall 2005 release of EnergyPlus.  
> 
> Until then, please tell me more about the system you
> wish to model.  What will 
> this heat pump serve - domestic hot water, space
> heating, space cooling?  Will 
> the air-side source/sink be inside the building or
> outdoors?
> 
> On 1 May 2005, at 17:54, Pedro Rodrigo wrote:
> 
> > Dear all.
> > I have realized that there is not a model available
> in
> > EP for a reversible cycle air to water heat pump
> > (central equipment).
> > I'm really interested in using this unit in my EP
> > simulations.
> > Do you have a creative idea to implement something
> > similar to this kind of equipment?
> > Thanks a lot,
> > Regards,
> > 
> > Pedro Manuel Rodrigo Cruz
> > University of Jaen, Spain
> > 
> > 
> > 
> > ______________________________________________ 
> > Renovamos el Correo Yahoo! 
> > Nuevos servicios, más seguridad 
> > http://correo.yahoo.es
> > 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are not allowed -- please post any files
> to the appropriate folder
> > in the Files area of the Support Web Site.
> > 
> > Yahoo! Groups Links
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> 
> 
> 
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support      
> EnergyPlus-Support@xxxxxxxx
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files
> to the appropriate folder in the Files area of the
> Support Web Site.
> 
> 
> 
> 
> ---------------------------------
> Yahoo! Groups Links
> 
>    To visit your group on the web, go to:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
>    To unsubscribe from this group, send an email to:
> EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
>    Your use of Yahoo! Groups is subject to the Yahoo!
> Terms of Service.
> 
> Pedro Manuel Rodrigo Cruz
> University of Jaen, Spain
> 
> 
> 
> ______________________________________________ 
> Renovamos el Correo Yahoo! 
> Nuevos servicios, más seguridad 
> http://correo.yahoo.es
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/