Judging from the warning message, you've input a door to only one of the
paired interior surfaces. You should add a mirror door on the other interior
surface as well.
Joe
----- Original Message -----
From: "Ali_Ajmi" <ajmi70kw@xxxxxxxxxxx>
To: "EnergyPlus" <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Tuesday, May 10, 2005 9:06 AM
Subject: [EnergyPlus_Support] Warnings
> Dear all,
> I have created IDF file for five zone office building which have no errors
or warning till I add two doors. One in the south surface of the North zone
and an opposite to that a door in the north surface of the South zone i
checked the vertices's for both the doors and the zones i could not fined
any wrong entries. Could any one help to know the source of that errors:
>
> ** Warning ** InterZone Surface Areas do not match as expected and
might not satisfy conservation of energy:
> ** ~~~ ** Area=74.2 in Surface=ZONE NORTH SURFACE SOUTH,
Zone=ZONE NORTH
> ** ~~~ ** Area=81.0 in Surface=ZONE INTERIOR SURFACE NORTH,
Zone=ZONE INTERIOR
> ** Warning ** InterZone Surface Areas do not match as expected and
might not satisfy conservation of energy:
> ** ~~~ ** Area=74.2 in Surface=ZONE SOUTH SURFACE NORTH,
Zone=ZONE SOUTH
> ** ~~~ ** Area=81.0 in Surface=ZONE INTERIOR SURFACE SOUTH,
Zone=ZONE INTERIOR
>
> Best Regards
> Ali
>
>
>
> ---------------------------------
> Yahoo! Messenger - want a free & easy way to contact your friends
online?
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/