With this input, both conditions must be true for the shade to be deployed.  
The schedule must be >0.0 and the zone air temperature must be >23.8 (the 
setpoint value).  Is the shade active at times when the schedule is zero?

Mike


On 27 May 2005, at 9:54, Miguel Angel Pascual Buisan wrote:

> Hello,
> 
> 
> 
> 
> 
> I am running a simulation with a "WindowShadingControl" that should be
> controlled by "Schedule" AND "OnIfHighZoneAirTemp".  
> 
> 
> 
> 
> 
> The problem is that the control is only responding to the
> "OnIfHighZoneAirTemp" condition. Any suggestion about this?
> 
> 
> 
> 
> 
> 
> 
> WINDOWSHADINGCONTROL, CONTROL ON INCIDENT SOLAR, !- Name of Shading Control
> 
>    ExteriorShade, !- Shading Type
> 
>    sun guard con persiana exterior, !- Name of construction with shading
> device
> 
>    OnIfHighZoneAirTemp, !- Shading Control Type
> 
>    Sombra Solo Verano, !- Schedule name
> 
>    23.8, !- Setpoint 
> 
>    YES, !- Shading Control Is Scheduled
> 
>    NO, !- Glare Control Is Active
> 
>    , !- Material Name of Shading Device
> 
>    , !- Type of Slat Angle Control for Blinds
> 
>    ; !- Slat Angle Schedule
> 
> 
> 
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/