Dear All,
I have imitated the 5ZoneVAVauto example in my equipment side, however, I got some errors and warnings that i can not sort out. Any advice will be greatly appreciated.
Program Version,EnergyPlus 1.2.1.022, 02/06/2005 16:16,IDD_Version 1.2.1.022
** Severe ** Missing reference temperature setpoint for Mixed Air Set Point Manager MIXED AIR AND COIL EXIT TEMP MANAGER 1
** ~~~ ** Node Referenced =VAV SYS 1 OUTLET NODE
** ~~~ ** use a Set Point Manager to establish a setpoint at this node.
** Severe ** Missing temperature setpoint for DX unit DX COOLING COIL SYSTEM 1
** ~~~ ** use a Set Point Manager to establish a setpoint at the unit control node.
** Severe ** Missing temperature setpoint for heating coil MAIN HEATING COIL 1
** ~~~ ** use a Set Point Manager to establish a setpoint at the coil temperature setpoint node.
** Severe ** Missing temperature setpoint for economizer controller OA CONTROLLER 1
** Severe ** Node Referenced (in Controller)=MIXED AIR NODE 1
** ~~~ ** use a Set Point Manager to establish a setpoint at the mixed air node.
** Fatal ** Previous severe set point errors cause program termination
************* Fatal error -- final processing. More error messages may appear.
************* Testing Individual Branch Integrity
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
** Warning ** Node Connection errors shown during "fatal error" processing may be false because not all inputs may have been retrieved.
** Warning ** Potential Node Connection Error for object COIL:ELECTRIC:HEATING, name=ZONE INTERIOR ZONE COIL
** ~~~ ** Node Types are still UNDEFINED -- See Branch/Node Details file for further information
** ~~~ ** Inlet Node : ZONE INTERIOR ZONE COIL AIR IN NODE
** ~~~ ** Outlet Node: ZONE INTERIOR IN NODE
** Warning ** Node Connection Error for object COIL:ELECTRIC:HEATING, name=ZONE INTERIOR ZONE COIL
** ~~~ ** Air Nodes not on any Branch or Parent Object
** ~~~ ** Inlet Node : ZONE INTERIOR ZONE COIL AIR IN NODE
** ~~~ ** Outlet Node: ZONE INTERIORNIN NODE
************* There were 2 node connection errors noted.
*************
Regards
Ali
---------------------------------
How much free photo storage do you get? Store your holiday snaps for FREE with Yahoo! Photos. Get Yahoo! Photos
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/