Re: [EnergyPlus_Support] overhang - Surface:Shading:Attached



In the BUILDING object, check the Solar Distribution field.  If it is set to 
"MinimalShadowing", then the overhang will not work.  If it is set to one of 
the FullExterior* options, then turn on REPORT, Surfaces, Details and check the 
tilt and azimuth of every surface.  Also, check the TransSchedShadowSurf field 
on the shading surface.  If this is always 1, the surface trasmits all solar 
and has no effect.  This schedule should be 0 for opaque shading surfaces.

Mike


On 2 Jun 2005, at 17:10, Arno Dentel wrote:

> Hello.
> I compared two identical rooms, but one of them has an overhang.
> As report variabel I chose "Zone Transmitted Solar" but the amount of 
> solar radiation entering the zone is the same.
> Has anybody a hint for me?
> 
> Arno.
> 
> 
> 
> Surface:Shading:Attached,
>     overhang,                !- User Supplied Surface Name
>     Sued,                    !- Base Surface Name
>     ,                        !- TransSchedShadowSurf
>     4,                       !- Number of Surface Vertex Groups --
> Number of (X,Y,Z) groups in this surface
>     -10,                     !- Vertex 1 X-coordinate {m}
>     -10,                     !- Vertex 1 Y-coordinate {m}
>     3,                       !- Vertex 1 Z-coordinate {m}
>      10,                     !- Vertex 2 X-coordinate {m}
>     -10,                     !- Vertex 2 Y-coordinate {m}
>     3,                       !- Vertex 2 Z-coordinate {m}
>      10,                     !- Vertex 3 X-coordinate {m}
>     0,                       !- Vertex 3 Y-coordinate {m}
>     3,                       !- Vertex 3 Z-coordinate {m}
>     -10,                     !- Vertex 4 X-coordinate {m}
>     0,                       !- Vertex 4 Y-coordinate {m}
>     3;                       !- Vertex 4 Z-coordinate {m}
> 
> 
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/