AW: [EnergyPlus_Support] overhang - Surface:Shading:Attached
Mike,
my inputs are correct. Only the field ?sun exposure? of the base surface
was set to ?no sun?.
What does EneryPlus calculate by setting the sun exposure to ?no sun?.
Only diffuse radiation or no radiation?
Arno
-----Ursprüngliche Nachricht-----
Von: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Im Auftrag von Michael J.
Witte
Gesendet: Freitag, 3. Juni 2005 00:02
An: EnergyPlus_Support@xxxxxxxxxxxxxxx
Betreff: Re: [EnergyPlus_Support] overhang - Surface:Shading:Attached
In the BUILDING object, check the Solar Distribution field. If it is
set to
"MinimalShadowing", then the overhang will not work. If it is set to
one of
the FullExterior* options, then turn on REPORT, Surfaces, Details and
check the
tilt and azimuth of every surface. Also, check the TransSchedShadowSurf
field
on the shading surface. If this is always 1, the surface trasmits all
solar
and has no effect. This schedule should be 0 for opaque shading
surfaces.
Mike
On 2 Jun 2005, at 17:10, Arno Dentel wrote:
> Hello.
> I compared two identical rooms, but one of them has an overhang.
> As report variabel I chose "Zone Transmitted Solar" but the amount of
> solar radiation entering the zone is the same.
> Has anybody a hint for me?
>
> Arno.
>
>
>
> Surface:Shading:Attached,
> overhang, !- User Supplied Surface Name
> Sued, !- Base Surface Name
> , !- TransSchedShadowSurf
> 4, !- Number of Surface Vertex Groups --
> Number of (X,Y,Z) groups in this surface
> -10, !- Vertex 1 X-coordinate {m}
> -10, !- Vertex 1 Y-coordinate {m}
> 3, !- Vertex 1 Z-coordinate {m}
> 10, !- Vertex 2 X-coordinate {m}
> -10, !- Vertex 2 Y-coordinate {m}
> 3, !- Vertex 2 Z-coordinate {m}
> 10, !- Vertex 3 X-coordinate {m}
> 0, !- Vertex 3 Y-coordinate {m}
> 3, !- Vertex 3 Z-coordinate {m}
> -10, !- Vertex 4 X-coordinate {m}
> 0, !- Vertex 4 Y-coordinate {m}
> 3; !- Vertex 4 Z-coordinate {m}
>
>
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate
folder in the Files area of the Support Web Site.
_____
Yahoo! Groups Links
* To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
* To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscri
be>
* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
<http://docs.yahoo.com/info/terms/> Service.
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/