Re: [EnergyPlus_Support] About the zone temperature



In your Zone Sizing object for the 3 undersized zones, input a zone 
sizing factor > 1.

Fred Buhl

energypluser wrote:

>Dear all
>
>    I used a electric chiller to serve six Fan Coil Unit: 4 pipe for 
>conditioning six different thermal zones. All the fan coil units are 
>autosized, and the zone temperature set to 24C during the conditioning 
>time. But the design day simulation results shows that the zone 
>temperature in three zones floats up to 26C, while the temperature of 
>the other three zones retains 24C. 
>    I think the chiller has adequate cooling capacity. I did not use 
>any controller to distribute the chilled water to fan coil unit.Because 
>the HVAC system is composed of fan coil units and chiller. How can I 
>increase the chilled water flow rate for the three heater zones ?    
>
>
>
>
>
>The primary EnergyPlus web site is found at:
>http://www.energyplus.gov
>
>The group web site is:
>http://groups.yahoo.com/group/EnergyPlus_Support/
>
>Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
> 
>Yahoo! Groups Links
>
>
>
> 
>
>
>
>  
>


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/