[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: About the cooling load and heating load repot



Dear Fred

How can I get the cooling & heating load output of each zone hourly 
through the report variable in E+?
I have studied the rdd.file, and I can not find such vairables.
Is it feasible for me to sum up some report variables for the 
purpose?
Thank you in advance

                                                      charles

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, fred buhl <wfbuhl@l...> 
wrote:
> No, they will not be equal. The cooling (for instance) done by the 
fan 
> coil is is the
> energy removed from the airstream going through the fan coil. Of 
course 
> the fan coil
> will attempt to meet the zone cooling load, but it has to remove 
fan 
> heat gain and deal
> with with the heat addition or loss due to ventilation air.
> 
> Fred Buhl
> 
> energypluser wrote:
> 
> >Dear all
> >
> >I used one fan coil unit:4 pipe for conditioning a zone. Does the 
zone 
> >cooling load equal to the fan coil total cooling rate at every 
time 
> >step ?
> >How about the heating load? Does it equal to the coil heating 
rate ? 
> >
> >Thank you in advance
> >
> >
> >
> >
> >
> >The primary EnergyPlus web site is found at:
> >http://www.energyplus.gov
> >
> >The group web site is:
> >http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> >Attachments are not allowed -- please post any files to the 
appropriate folder in the Files area of the Support Web Site.
> > 
> >Yahoo! Groups Links
> >
> >
> >
> > 
> >
> >
> >  
> >




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/