Mike could you help me finding the energy code for the USA of the typical office lighting and infiltration.
Thanks
"Michael J. Witte" <mjwitte@xxxxxxxx> wrote:
1. This is a reheat system, so the reheat coils pick up the remaining heating
load, raising the 18C central supply air to a higher temperature.
2. Heating coils are always placed directly on the branch, DX coils are not.
Gas and electric heating coils can control themselves by specifiying a control
node which has a valid setpoint on it. DX coils cannot, so they must be
enclosed in another component such as DX System:Air Loop (see example file
5ZoneAutoDXVAV.idf). Hot water coils require a CONTROLLER:SIMPLE.
3. I am not sure what you mean by this question. A node only has meaning if
it is used by a component.
4. Do a simulation with DAYLIGHTING in it and consult the rdd output file for
daylighting related variables (illuminances, glare index, lighting power
multiplier, etc.)
5. Do you mean typical or most efficient available? This may vary regionally.
I suggest consulting the applicable energy codes for the location you are
modeling.
Mike
On 8 Jul 2005, at 10:07, Ali_Ajmi wrote:
> Hi All,
>
> I am simulating a five zone building with VAV reheat system. I have several
> questions that I could not understand how to tackle it. These questions are as
> follows:
>
> 1. VAV system outlet temperatures sated as default between 12 to 18 C.
> How would be
> zones heated if maximum is 18 and the zone set point temperature
> is 20 C?
>
> 2. In Unitary DX System:Air loop the cooling coil is only specified
> what a bout the
> heating coil? Is heating coil using same spec. of the cooling
> coil?
>
> 3. If there are nodes which are not referenced, Is this node not
> integrated with system?
>
> 4. Which report variables that can be used to show the daylighting
> effects?
>
> 5. What is the best lighting design level of office building per meter
> squares?
>
> Thanks in advance.
>
> Ali
>
>
>
>
> ---------------------------------
> How much free photo storage do you get? Store your holiday snaps for FREE with
> Yahoo! Photos. Get Yahoo! Photos
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
---------------------------------
Yahoo! Messenger NEW - crystal clear PC to PCcalling worldwide with voicemail
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/