Re: [EnergyPlus_Support] Error message on flow rate
See if this further error detection will help you:
Program Version,EnergyPlus 1.2.2.033, 7/17/2005 4:28 PM,IDD_Version 1.2.2.033
** Warning ** No Controllers for Air System:AHU37 PRIMARY AIR LOOP
** Severe ** Inlet parameters for plant demand side splitter are
not physically possible
** ~~~ ** Problem in input for plant demand side HOT WATER PLANT LOOP
** ~~~ ** The maximum flow out of the splitter [10.45] is
less than the minimum inlet flow [15.86]
** ~~~ ** Flow rate inputs for the loop do not match flow
requirements of the various branches/components
** ~~~ ** Check your flow rates and make sure that flow
balances between the splitter inlet and outlets
** Fatal ** EnergyPlus terminated due to reason stated above
************* Fatal error -- final processing. More error
messages may appear.
************* Testing Individual Branch Integrity
=====> especially this:
** Severe ** Non-unique node name found, name=AHU37 RETURN AIR INLET
** ~~~ ** ..1st occurence in Branch=AHU37 MAIN AIR LOOP BRANCH
** ~~~ ** ..duplicate occurrence in Branch=AHU37 RETURN AIR BRANCH
** Severe ** Branch(es) did not pass integrity testing
Linda
EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team
[Non-text portions of this message have been removed]
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/