Is this a zone coil? Take a look at your Zone Sizing input and see if
the design
leaving humidity ratio looks appropriate for your climate/location
Fred Buhl
dreamerfish8146 wrote:
>Dear all:
> I wondered what this warnning means:
>** Warning ** SizeWaterCoil: Coil="COIL-ZONE", Cooling Coil has leaving
>humidity ratio > entering humidity ratio.
> ** ~~~ ** ..will be sized for 50% of design entering humidity
>ratio.
> The temperature difference between the supply cooling water and
>return water is less than 1 degree.And my design loop delta t is 5
>degree.I don't know why it's so small.I need your suggestion.
> Thank you!
>
>
>
>