Re: [EnergyPlus_Support] Purchase Air problem



Add the following report variables to see how the system controls are operating:

  Zone/Sys Thermostat Heating Setpoint
  Zone/Sys Thermostat Cooling Setpoint
  Zone/Sys Thermostat Control Type

Reviewing the results shows that the purchased air is meeting these requests.  
In the control type schedules there are several months where the control type 
is being set to zero which means no heating or cooling should operate.  

Mike


On 25 Jul 2005, at 15:31, ?©?Î?Ø wrote:

> Hello.
> I am using Purchase Air but it does not work consistently.
> The Zone MAT meet the setpoint temperature only during some days in the 
> heating and cooling period.
> Uploaded the file: PurchAir Problem
> Could anybody please advice whether it is problem with my setting?
> Thank you!
> 
> PuiWah
> 
> 
> 
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
> 
> Yahoo! Groups Links
> 
> 
> 
> 
> 
> 
> 
> 



========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support      
EnergyPlus-Support@xxxxxxxx




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/