[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Harbour Building



At 06:44 PM 8/15/2005, wing sun lee wrote:
>I have check my idf thoroughly, but I can't tackle down the "Severe" error.
>Would you mind helping me to address or point out that.

I'm not sure which severe error you are referring to, there are so many.

The warnings about zero load for the zone sizing could be a big problem.

Then, there are these:
    ** Severe  ** Node SUPPLY AIR INLET NODE-ZONEGF3 connects to no component
    **   ~~~   ** Occurs in Supply Air Path=SAPATH-CAV GA G/F
    ** Severe  ** An outlet node in  Air Primary Loop CAV SYSTEM-AHU 
GA G/F is not connected to any zone
    **   ~~~   ** Could not match ZoneEquipGroup Inlet 
Node="ZONEEQUIPINLETNODE-CAV GA G/F" to any Supply Air Path or controlled zone
    ** Severe  ** Node SUPPLY AIR INLET NODE-ZONEGF4 connects to no component
    **   ~~~   ** Occurs in Supply Air Path=SAPATH-CAV GB G/F
    ** Severe  ** An outlet node in  Air Primary Loop CAV SYSTEM-AHU 
GB G/F is not connected to any zone
    **   ~~~   ** Could not match ZoneEquipGroup Inlet 
Node="ZONEEQUIPINLETNODE-CAV GB G/F" to any Supply Air Path or controlled zone
    ** Severe  ** Node DAMPER INLET NODE-ZONEGF6 connects to no component
    **   ~~~   ** Occurs in Supply Air Path=SAPATH-VAV GA G/F

which seem to be somewhat self-explanatory?


Linda

EnergyPlus WebSite: http://www.energyplus.gov
Owner: EnergyPlus_Support list
Member: EnergyPlus Development Team



[Non-text portions of this message have been removed]



------------------------ Yahoo! Groups Sponsor --------------------~--> 
<font face=arial size=-1><a href="http://us.ard.yahoo.com/SIG=12hncs5g4/M=362335.6886445.7839731.1510227/D=groups/S=1705007389:TM/Y=YAHOO/EXP=1124209052/A=2894361/R=0/SIG=13jmebhbo/*http://www.networkforgood.org/topics/education/digitaldivide/?source=YAHOO&cmpgn=GRP&RTP=http://groups.yahoo.com/";>In low income neighborhoods, 84% do not own computers. At Network for Good, help bridge the Digital Divide!</a>.</font>
--------------------------------------------------------------------~-> 

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/