Check the location and design day objects (time zone, clearness), check the
thermostat schedules, check the internal gain schedules. Does the cooling
design day have a range of temperature, or is it constant? Is the clearness >
0? In the RUN CONTROL, set "Do design day simulation" to YES, and turn on
reporting of thermostat setpoints, internal gains, weather data, etc. This
should help determine where the problem is.
Mike
On 6 Sep 2005, at 16:32, hbn_pch wrote:
> Dear all,
> i'm puzzled for the zone design cooling load after a simulation.i
> found that time of the peak cooling load of some zones is intricate.for
> example:
>
> Zone Sizing, 1F_9, Cooling, 895.09 , 0.66339E-01, 0.66339E-01,
> SUMDAY, 00:15:00, 29.600 , 0.19897E-01
>
> Zone Sizing, 1F_4, Cooling, 1253.5 , 0.92903E-01, 0.92903E-01,
> SUMDAY, 00:30:00, 29.600 , 0.19897E-01
>
> these two zones faces west,but the time of peak is 00:15:00,is it
> possibel?
>
> thanks
> pch
>
>
>
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder
> in the Files area of the Support Web Site.
>
> Yahoo! Groups Links
>
>
>
>
>
>
>
>
========================================================
Michael J. Witte, GARD Analytics, Inc.
EnergyPlus Testing and Support
EnergyPlus-Support@xxxxxxxx
------------------------ Yahoo! Groups Sponsor --------------------~-->
Most low income households are not online. Help bridge the digital divide today!
http://us.click.yahoo.com/cd_AJB/QnQLAA/TtwFAA/dkFolB/TM
--------------------------------------------------------------------~->
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/